Bang on there Mr Small, great memory.
This is the intepretation given back in 2002, still stands today. I also have a video of applicaiton of earthing that i made a few years ago that I’ll post up as link here.
Interpretation on Rule 703 and Minimum Approach Distances
Background
An interpretation was requested on the Minimum Approach Distance (MAD) requirements of SR-EI rule 703.
The specific issue involves working on the de-energised contact of a DDO when the line termination is energised. In this circumstance the de-energised contact is only 270mm from the energised contact, whereas rule 703 requires a MAD (for 11kV) of 300mm.
Interpretation
MAD’s as prescribed in rule 703 are minimum distances within which an employee must not encroach. The rule applies to any part of the body of the person, and to anything which is in contact with the person, other than a live work tool rated for the voltage. (Note that a temporary earth is not a live work tool).
The distances are established by taking into account the following;
· The behaviour of electrical power systems under steady state and transient conditions
· Determining the distances in air necessary to avoid electrical flashover under these conditions
· Providing additional allowance for inadvertent movement of the person and/or the electrical equipment
For 11kV the distance requirements for electrical considerations only are up to 66mm. The balance of the MAD is provided for inadvertent movement.
It should be noted that the standard Australian requirements for 11kV are for a MAD of 700mm for all persons. (They require a minimum distance for inadvertent movement of 600mm in all circumstances). This distance can be reduced under very controlled conditions, provided the person is ‘authorised’, ie competent.
DDO’s
The Safety Strategy & Policy Group has recently considered the MAD as applied to DDO’s as a result of an issue brought to its attention which involves the application and/or removal of temporary earths to lugs fitted to DDO’s. Such application or removal of the earth requires encroachment within the MAD. The SS&P Group confirmed during its considerations that the MAD’s provided in rule 703 are the minimum to be applied.
This matter is dealt with in the June issue of the Safety Rules Newsletter.
Conductors Connected to DDO’s
The MAD applies only to the distance of the employee (and any tool held) from the nearest live conductor, or live part. Work on a conductor which has a termination within the MAD is safe provided the break between the live and de-energised conductors meets the minimum distance for electrical flashover purposes, and the conductor being worked on is isolated and earthed.
Interpretation issued by EEA Safety Strategy & Policy Group
17<sup>th</sup> July 2002