Use of HV Live Line Procedures on Isolated Lines and Equipment
The National Committee on Live Work (NCLW) has also been asked about the use of high voltage live line work methods on isolated lines and equipment.
Discussion is around the point that by isolating lines and equipment, an additional level of control is applied when undertaking HV Live Line work.
The NCLW has considered this and supports isolation, as a practical step in minimising risk of harm.
However this support is subject to all the following criteria being met:
- The isolation is recorded as a control on the HV live line work permit, similar to how industry record the application of a recloser block. Note: a HV live line permit and access permit shall not be issued for the same work. ·
- The work is undertaken in strict compliance with the HV live line work method being used.
- At all times, the isolated lines and equipment must be treated as live and the HV live line worker must not encroach the live line minimum approach distance applicable to the work method.
- Work shall stop immediately when a problem arises and must not recommence until the problem is resolved.
- This work shall be monitored and audited in accordance with live line requirements.