Guest15 April 2024 at 2:39 pmHi Robert
Our sticks are rated to full working voltage, however we still require the use of rated Insulated Gloves as well for secondary protection (and yes our workers also stabilise the stick with their thighs).
The EEA Technical Guide: Portable Equipment for Work On or Near Conductors states in Section 8 Operating and Measuring Sticks or Rods: ‘When using operating sticks or rods the minimum approach distance (MAD) applicable to the voltage shall not be encroached by the user or any part of the stick or rod which the user is in contact with, and which is not proven to be insulating. This requires that the insulating section is of sufficient length to meet these criteria’.
So the Technical Guide does not require secondary protection if proven to be insulating – Hope this helps?
Stephen.