  • Graeme Jackson

    Member
    29 June 2021 at 5:39 pm

    Hi James, Not sure if this is covered by ECP 34, but the separation of services pillars and vaults seems to have been missed. The area on section boundaries is hotly contested for water meters, water tobies, telecommunications, fibre and of course electricity. A fault in an electricity pillar may not be apparent until the water services or fibre teams start digging and then step and touch potentials may become an issue, even without metal water pipes being part of the equation. Should ECP34 stipulate a safe separation distance between services? Interested in other feedback.