    Posted by Rebeca Clifton on 7 October 2024 at 8:59 am

    Hello – is anyone able to share what PPE you require your staff to wear when carrying out LV and HV switching on your Network? We are reviewing our requirements and are keen to know what others do.

    Thanks, Rebeca

    Rebeca Clifton replied 1 year, 5 months ago 3 Members · 4 Replies
  • 4 Replies
  • Stephen Albrecht

    Member
    7 October 2024 at 9:42 am

    Hi Rebeca,

    As per Appendix B in our PPE Standard (attached).

    Regards

    Stephen Albrecht

     

  • Stephen Small

    Member
    7 October 2024 at 1:20 pm

    Hi Rebecca

    Before looking at what we do, you will need to determine what you need.

    Each network has a unique electrical fault context; as it is built using similar but not the same equipment, which may perform differently during a fault. (for example, one EDB may have Neutral Earth Resisters at every Zone substation to limit fault current, and another EDB might not; different models of RMU may be able to be operated remotely, or not).

    Your engineers should undertake Arc Flash calculations for your equipment, which will then guide you to the necessary minimum requirements for Arc Rated PPE. The EEA Arc Flash Guide is a useful reference.

    Like you we are reviewing our PPE standard, and we are using our arc flash calculations to inform our thinking.

    regards

    Stephen.

  • Rebeca Clifton

    Member
    7 October 2024 at 2:16 pm

    Thanks Stephen.

  • Rebeca Clifton

    Member
    7 October 2024 at 2:21 pm

    Thanks Stephen – the engineering team is involved in our discussions around this and I’ll pass on your feedback.