Reply To: Applying portable earthing to EDO on 22kV network

  • Bill Doig

    Member
    19 February 2026 at 1:36 pm

    We fit new EDO’s with earthing spigots so they’re below the stated distance. We don’t allow snap on earths to be used in these situations as when pushing the clamp off, there’s a risk of contacting the live side of the EDO