Class 1 gloves

  • Class 1 gloves

    Posted by Bill Doig on 30 March 2021 at 10:41 am

    Where does your company use these besides work on de-energised and earthed HV lines. EDO switching using insulated sticks and RMU/ABS switching at 11kV? Line of thought is it’s not stipulated in the SM-EI and the voltage line to earth is 6.35 kV.

    Regards

    Bill Doig

    paul-smeetstopenergy-co-nz replied 3 years, 8 months ago 3 Members · 4 Replies
  • 4 Replies
  • Graeme Johnson

    Member
    6 April 2021 at 3:01 pm

    Bill

    We use class 1 as you describe – HV shuts, earthing, single phase HV operation

    Detailed as below:

    • Bill Doig

      Member
      3 May 2021 at 10:49 am

      Given I had yours G, I was hoping for a little more industry feedback. We are proposing to include 11kV three phase operations as the line to earth voltage is only 6.35kV

      • paul-smeetstopenergy-co-nz

        Member
        11 June 2021 at 1:10 pm

        <div>Hi Bill, TE requirements:</div>

        a) Minimum class 00 when accessing, operating, testing, earthing or working on all LV equipment that has not had earths applied at all isolation points including all sources of potential inadvertent livening

        b) Minimum class 1 when operating, testing or earthing all 11kv HV equipment

        c) Minimum class 2 when operating, testing or earthing all 33kv HV equipment

  • paul-smeetstopenergy-co-nz

    Member
    31 May 2021 at 4:12 pm

    We are currently looking into this as part of revising our PPE Guide.

    Will post here following our review of the applicable standard, when I get hold of it.

    Note ECP 46 2.6.8 & 2.6.9 gives some guidance but not sure if this applies to just live line or across the board